Pup7
Electrical
- Feb 14, 2008
- 4
We have two 6KV XFR that feed two individual 380V MCCs with an ATS that closes the Tie brkr between them whenever one of the XFR feeders fail. Last night one of the XFR feeders tripped on over current and we found the XFR that tripped is pulling five times (300amps) on the primary side then the other XFR, while the Tie brkr is open. When we open the XFR feeder and close the tie putting all the load on the other XFR, the amperage on that XFR goes from 65 amps up to 160 amps. which indicates normal load. We can close the brkr on the XFR that tripped without any problem, but as soon as we close the secondary side brkr it will go into this high current condition on the primary, are we looking at a possible secondary winding fault problem, that only the primary side protection is picking up?. Any help will be appreciated at this time, as we are in the process of further investigation at the present time.