Has anyone experienced compatibility / sizing issues when useing the powerflex 7000 and a backup genertor system that operates in the island mode only??
History: Recent plant renovations included installing 4 Powerflex 7000 drives driving loads from (2)500 (1)700 and (1) 800hp. Back up generator power supplied via Detroit Diesel 2MW genset 7M4374. There is no line / generator / utility side harmonic filters / traps or inductive loadbanks on the oem supplied system.
This station is unmanned and needs to operate with no onsite operator action.
When operating against the utility with any pump combination everything is fine.
When operating the 2 500hp drives on the generator everything is fine.
However when we try and start the 700hp unit when the (2) 500hp units are already running the generator begins to oscillate and become unstable and unless operator action is taken to decrease the load, if no action is taken the generator breaker trips the station out leaving us with no power. The 700hp unit can run by itself on the generator. The 800hp cannot run with any pump combination on the generator it can run by itself.
PF with these drives is leading, spec'd to be unity to .95 lagging.
Design / specs required the ability to run any combination of 3 pumps
What we've tried:
AB has tried resizing the caps / inductors on the drives. to no avail.
Tried installing a 450 kvar inductive load bank that helped with the pf and some harmonics however it didnot affect the runnability issues.
Design eng / contractor / generator / AB, are all pointing the blame to somebody else and not coming up with an answer.
Design eng. recommends putting in differnt drive mfg. as AB is the only mfg useing caps / inductors on the front end and they believe this causing a resonance issue
AB recommends upsizing generator.
AB has stated from the begining that they were unaware that the system would be operating on a generator and if they new they would have recommended sizing the generator for 200% station load.
Has anyone else ever experinecd this, heard the 200% recommendation have real world exp with this problem?
Sorry for the long post
Thanks
Darrin
History: Recent plant renovations included installing 4 Powerflex 7000 drives driving loads from (2)500 (1)700 and (1) 800hp. Back up generator power supplied via Detroit Diesel 2MW genset 7M4374. There is no line / generator / utility side harmonic filters / traps or inductive loadbanks on the oem supplied system.
This station is unmanned and needs to operate with no onsite operator action.
When operating against the utility with any pump combination everything is fine.
When operating the 2 500hp drives on the generator everything is fine.
However when we try and start the 700hp unit when the (2) 500hp units are already running the generator begins to oscillate and become unstable and unless operator action is taken to decrease the load, if no action is taken the generator breaker trips the station out leaving us with no power. The 700hp unit can run by itself on the generator. The 800hp cannot run with any pump combination on the generator it can run by itself.
PF with these drives is leading, spec'd to be unity to .95 lagging.
Design / specs required the ability to run any combination of 3 pumps
What we've tried:
AB has tried resizing the caps / inductors on the drives. to no avail.
Tried installing a 450 kvar inductive load bank that helped with the pf and some harmonics however it didnot affect the runnability issues.
Design eng / contractor / generator / AB, are all pointing the blame to somebody else and not coming up with an answer.
Design eng. recommends putting in differnt drive mfg. as AB is the only mfg useing caps / inductors on the front end and they believe this causing a resonance issue
AB recommends upsizing generator.
AB has stated from the begining that they were unaware that the system would be operating on a generator and if they new they would have recommended sizing the generator for 200% station load.
Has anyone else ever experinecd this, heard the 200% recommendation have real world exp with this problem?
Sorry for the long post
Thanks
Darrin