I am about to install a vessel with electric actuators. My client specified AC power and so I got AC actuators. Now he's saying there is a delay in getting AC to the site and he wants to use batteries, inverters, and Solar panels.
The application draws 1.25 A for a couple of seconds every couple of minutes. The whole load is 7.8 A-hr/day at 110 VAC (without allowances for dark, inverter load, etc). Now comes my confusion. When I'm sizing batteries I'm going to assume than an amp is an amp and I will need to provide a battery that can do 8 A-hr/day at 110V times allowances for the inverter, for dark, and for clouds (140W) and not some other calculation that gives me numbers between 0.4W and 275W.
David
The application draws 1.25 A for a couple of seconds every couple of minutes. The whole load is 7.8 A-hr/day at 110 VAC (without allowances for dark, inverter load, etc). Now comes my confusion. When I'm sizing batteries I'm going to assume than an amp is an amp and I will need to provide a battery that can do 8 A-hr/day at 110V times allowances for the inverter, for dark, and for clouds (140W) and not some other calculation that gives me numbers between 0.4W and 275W.