Practical guide for ground grid design

Status
Not open for further replies.

JLuc

Electrical
Mar 30, 2007
62
I'm working on the expansion of an outdoor substation, and I'm looking for a practical guide to design the new earth grid. I have limited information on the existing one. Earth resistivity tests are beeing done now.

Any suggestion on such a practical guide??

It's a 25 kV sub, with 2 txfos (25kV/4kV & 25kV/600V both resistance grounded), capacitor bank, breakers etc.., the actual fence will be moved about 20 feet out on each side.

Thank you

JL
 
Replies continue below

Recommended for you

A classical guides are the IEEE Std 80 for the US and other ANSI market place and CENELEC / IEC Std 479-1 for European countries and other IEC market places.
 
thanks for the suggestions.

the IEEE Std 80 helped a lot. Good "step by step" design procedure.

JL
 
The problem will be with the unknown existing grid. For safety in the expansion area, you could assume a minimal grid in the existing substation. If the expansion increases fault levels at the existing substation, however, you need to check to ensure that the existing substation is safe. I see two choices. First, locate the existing grid and ground rods. Second, install new grid wires and/or ground rods in the existing substation area. Neither option is easy, particularly in an energized substation.

The CDEGS 2003 Users' Group Conference included a paper on the Assessment of Earthing Systems at Existing Substations by Mark Davies and Matthew Taylor, Strategy & Solutions Ltd, UK. You might get information on this at the SES website If not, you could contact SES to get a copy.
 