Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

precast bearing on grade beam

  • Thread starter Thread starter tw
  • Start date Start date
Status
Not open for further replies.

tw

Structural
Joined
May 30, 2001
Messages
70
Location
US
I have a 12,000 lb 6" thick precast panels that will bear on my continuous grade beam. Assuming during erection there will be two bearing points that will each take 6k. The ledge (like brick dap) is 6" wide so panel bearing will be centered as close to edge of concrete as 2 1/2 inches. Let's say they use 4" bearing plate, what kind of shear failure plane would I be looking at? Similar to corbel analysis?

tw
 
To avoid the problem, put in temporary metal shim plates at 4 foot centers until the wall can be continuously grouted between it and the strip footing. No worries.

Mike McCann
McCann Engineering
 
Is the bearing direct onto the grade beam, or are bearing plates cast into the grade beam? While a loose bearing plate theoretically spreads the load at the bearing point, in reality the plate sits non-uniformly on high points. You may want to use elastomeric or similar bearing pads to be sure you are spreading the load as designed at each of the two main bearing points. If you assure transfer, then you can lengthen the bearing plates. That will help a little. You could also have. at each bearing point, two shim stacks about 18-24" apart with an adequately thick steel plate between them. That would spead the load.

Intermediate shim points present a similar issue in that the load, at least at some moments during installation, will bear only on two points (thats what defines a straight line - the panels will not deform to put load on the added points).

 
First, you need to check if your bearing has enough area that will not cause bearing failure in the ledge or in the grade beam.

Secondly, you can use shear friction analysis to design the reinforcing for the ledge.

You also may need to increase the load to allow for any sudden impact during erection.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top