For a slotted insert (JVI PSA type)with a strap anchor, would you expect any shear resistance along the length of the insert if the strap is properly tightened. Essentially you get a clamping force. I dont see any info from the mfg that suggests there is, but wondering if anyone knows about this.

Thanks
 
Replies continue below

Recommended for you

I was curious so I looked at their website. I dont see anything that indicates it was designed to resist a force in that direction or tested in that direction but the brochure does say to put a washer if you need vertical movement which suggests some resistance. Contact the manufacturer is the best only bet.

Screenshot_-_Copy_xvxyok.png
 
Thanks, that makes sense what they show. I will not rely on any capacity along the length.
 
I am saying along the length of travel. If the strap is tightened down, any resistance along the length of it from the clamping force.
 
Would it not defeat the purpose of the connection if it provided some resistance in that plane?
 
Not necessarily. It gives erection tolerances, but once installed, might want resistance in that direction for lateral movement, etc. The connection does not move up and down inside, etc.
 
Given the variables involved of all the different materials involved I think you are going down a path very few do. The square nut inside the connection moves up and down. If one were to torque the strap beyond hand tight I suppose you will get some friction, but that is not the intent JVI had when they came up with this connection.
 