This is same question as :
thread238-87685
However it occurs to me I made it more complicated than necessary by mentioning ferroresonant transformer.
Let's just assume it is a standard dry type transformer.
On a low voltage single-phase transformer, we experienced failure from turn-to-turn short which was believed to be due to thermal aging. We want to figure out what kind of testing we can do (on-line or off-line) to have maximum confidence that the sister unit transformers will operate reliably and we can detect similar degradation ahead of time. What periodic testing of dry type transformers is appropriate if maximum reliability is desired?
Megger testing is a given. 500vdc.
TTR – (ok let's assume I can't do that test and move on).
Doble test?
* DC Hi-pot or step voltage test? I know this is fairly common on rotating machines but less so I believe on transformers. We did test one to 2kvdc with no failure. However we are not sure whether the test itself may degrade the reliability of the future reliability of the transformer (we’re not worried about failing a transformer during a test, just worried about passing the test and failing later as a result of the test).
Excitation current?
Winding resistance?
I think excitation current and winding resistance pose some challenges because on 3-phase unit we compare phases. In this case we would have to compare sister units or trend over time. Would it be beneficial?
Tear-down visual inspection and re-assembly (somehwat intrusive and may introduce problems).
Infrared?
Any thoughts and opinions at all would be appreciated. I have some experience testing large oil-filled power transformers but none at all on the small transformers. Also interested in any relevant links or standards references.
Thanks.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
thread238-87685
However it occurs to me I made it more complicated than necessary by mentioning ferroresonant transformer.
Let's just assume it is a standard dry type transformer.
On a low voltage single-phase transformer, we experienced failure from turn-to-turn short which was believed to be due to thermal aging. We want to figure out what kind of testing we can do (on-line or off-line) to have maximum confidence that the sister unit transformers will operate reliably and we can detect similar degradation ahead of time. What periodic testing of dry type transformers is appropriate if maximum reliability is desired?
Megger testing is a given. 500vdc.
TTR – (ok let's assume I can't do that test and move on).
Doble test?
* DC Hi-pot or step voltage test? I know this is fairly common on rotating machines but less so I believe on transformers. We did test one to 2kvdc with no failure. However we are not sure whether the test itself may degrade the reliability of the future reliability of the transformer (we’re not worried about failing a transformer during a test, just worried about passing the test and failing later as a result of the test).
Excitation current?
Winding resistance?
I think excitation current and winding resistance pose some challenges because on 3-phase unit we compare phases. In this case we would have to compare sister units or trend over time. Would it be beneficial?
Tear-down visual inspection and re-assembly (somehwat intrusive and may introduce problems).
Infrared?
Any thoughts and opinions at all would be appreciated. I have some experience testing large oil-filled power transformers but none at all on the small transformers. Also interested in any relevant links or standards references.
Thanks.
=====================================