CUChalk
- May 4, 2017
- 1
My client is a concrete contractor that I work with frequently. He has an upcoming job with a very tight construction schedule and in order to save time he has suggested pre-fabricating the rebar mats in his shop using ASTM A706 Grade 60 rebar. The engineer involved with the project has stated that "welding rebar mats together goes against everything I've ever been taught". The contractor has asked me for help with references or anything that permit this. I personally haven't had any experience with this specific application so I went to the codes.
ACI 318-14 26.6.4.1(b): Welding of crossing bars shall not be used for assembly of reinforcement unless permitted by the licensed design professional.
The commentary talks about how tack welding can create a metallurgical notch effect that weakens the rebar, but indicates it's possible if welding operations are under continuous competent control.
Then I found ASTM A184 which seems to indicate a process that allows this to happen (indicates how often to weld and some other min. requirements). It doesn't specifically provide any welding procedures that are acceptable, nor does it rule any out. I've also seen that CRSI allows fusion welding to be done by special machinery, but that's not an option here.
What are your thoughts on allowing the contractor to weld the rebar solely for the purpose of saving time over field-tying? This reinforcing will be going in foundations/slabs supporting heavy industrial machinery.
Chalk
Chalk