uranotek
Electrical
- Apr 22, 2008
- 6
I am Electrical engineer looking for some hydraulic/mechanical advice on convenience of implementing pressure control by VFD in (3) 40 HP vertical turbine pumps.
The brand new booster Pumps station has never being in service for 10 years as city customers complain about the high rate/pressure releases a lot of sediment from the century old pipeline system.Other issues arise as potential leaks / ruptures in the pipeline. The older pumping system is still operating at a lower pressure.
The main contractor did not install any water supply pressure control devices such as VFDs, Backpressure valve, Recirculating control valve or reducing impellers diameter.
The motors are controlled through PLC and standard soft-starters/contactors I need to justify technical and economically the high cost of 3 VFDs
My questions are:
1- Considering the affinity laws (flow vs RPM ) and ( flow vs HP) What kind of consideration/limitations exist by implementing pressure control based on VFDs?
2- How to find out the min and max. permissible variation of Pump speed (rpm) from the pump's efficiency curve rated at 1780 rpm. In my research I found out some issues might appear on speed control affecting the pump and/or the motor efficiency, energy cost etc.
From the curve I checked that 2 pumps need to run (in parallel) to meet the target Head and GPM.
The brand new booster Pumps station has never being in service for 10 years as city customers complain about the high rate/pressure releases a lot of sediment from the century old pipeline system.Other issues arise as potential leaks / ruptures in the pipeline. The older pumping system is still operating at a lower pressure.
The main contractor did not install any water supply pressure control devices such as VFDs, Backpressure valve, Recirculating control valve or reducing impellers diameter.
The motors are controlled through PLC and standard soft-starters/contactors I need to justify technical and economically the high cost of 3 VFDs
My questions are:
1- Considering the affinity laws (flow vs RPM ) and ( flow vs HP) What kind of consideration/limitations exist by implementing pressure control based on VFDs?
2- How to find out the min and max. permissible variation of Pump speed (rpm) from the pump's efficiency curve rated at 1780 rpm. In my research I found out some issues might appear on speed control affecting the pump and/or the motor efficiency, energy cost etc.
From the curve I checked that 2 pumps need to run (in parallel) to meet the target Head and GPM.