pressure drop from a blower fan

Status
Not open for further replies.

hsolid100

Mechanical
Apr 10, 2014
6
Hi, any ideas on calculating the pressure drop from a blower fan inside a tube.
 
Replies continue below

Recommended for you

Get a catalog.
Look up the engineering data for your blower fan.


Mike Halloran
Pembroke Pines, FL, USA
 
??? Your question needs to be "clarified"

First, we assume you have some pipe or leak-proof vent duct with an in-line (axial) fan inside.

If there is no flow in the pipe, before the fan turns on, pressure upstream = pressure downstream = P0

If there is flow in the pipe, before the fan turns on, pressure upstream > pressure downstream due to flow losses through the fan blades. But this is meaningless, nobody can use a fan as a vent damper!

After the fan turns on, pressure upstream << pressure downstream calculated from the fan manufacturer tables of design efficiency at that pressure, temperature, gas type, and fan diameter. Pressure upstream will slightly less than the original static P0, but vent fans at normal flows and temperatures don't have a NPSH problem like fluid pumps do. Turbines can because they running near their max , vent fans "can" but only if they woefully sized wrong or the suction damper is shut.

 
Is the fan on or off?

Good luck,
Latexman

Technically, the glass is always full - 1/2 air and 1/2 water.
 
Reverse my << above into >>>

RACook said:
After the fan turns on, pressure downstream >> pressure upstream. Calculate this from the fan manufacturer tables of design efficiency at that pressure, temperature, gas type, and fan diameter.
 