I am looking at a 6 story apt bldg that will need a fire pump to get the 100 psi residual @ top of standpipe. My customer has suggested using a 6" pressure reducing valve in the basement on the 6" main supply to the standpipes vs installing individual pressure reducing valves on each floor.
I cannot find anything that says I cannot do this, the calcs work out to allow this to happen. Are there any codes I am missing that say this cannot be done? I am looking at the 6" Tyco PRV-1.
Thanks