Hi,
I am working in a project where there is a pipeline filled with water and traces of glycol at 50ºC. That pipeline can be blocked and the client suggests a thermal relief valve. I am trying to justify if this thermal relief valve is needed or not.
As per API 521 (6th edition, 2014) section 4.4.12.4:
Where the system under consideration for thermal relief consists of piping only (does not contain pressure vessels or heat exchangers), a PRD might not be required to protect piping from thermal expansion if any of the following apply:
c) The fluid temperature is greater than the maximum temperature expected from solar heating [usually approximately 60 °C to 70 °C (approximately 140 °F to 160 °F)] and there are no other heat sources such as heat tracing (note that fire is generally not considered when evaluating pressure-relief requirements for piping);
If we consider 70º as the maximum temperature expected from solar heating (our pipeline is not in the upper part of the rack, but we cannot say which is the maximum T expected), we can't consider this point as our case.
d) The estimated pressure rise from thermal expansion is within the design limits of the equipment or piping.
I used the equation (3) from API 521 (6th edition, 2014) section 4.4.12.4 for pressure rise due to simultaneous heating of the pipe and blocked-in liquid and I am getting a pressure rise of 49 kg/cm2 by the increase of 1ºC of temperature.
I also calculate the temperature rise due to solar radiation (taking 1.04kW/m2 for intensity of solar radiation in accordance with API 521) and I am getting a temperature rise of 5ºC, resulting in a pressure increase of 245 kg/cm2 based on the results of pressure increase I mention previously.
This does not make much sense so I am wondering if this is correct.
Does anyone have any thoughts?
I am working in a project where there is a pipeline filled with water and traces of glycol at 50ºC. That pipeline can be blocked and the client suggests a thermal relief valve. I am trying to justify if this thermal relief valve is needed or not.
As per API 521 (6th edition, 2014) section 4.4.12.4:
Where the system under consideration for thermal relief consists of piping only (does not contain pressure vessels or heat exchangers), a PRD might not be required to protect piping from thermal expansion if any of the following apply:
c) The fluid temperature is greater than the maximum temperature expected from solar heating [usually approximately 60 °C to 70 °C (approximately 140 °F to 160 °F)] and there are no other heat sources such as heat tracing (note that fire is generally not considered when evaluating pressure-relief requirements for piping);
If we consider 70º as the maximum temperature expected from solar heating (our pipeline is not in the upper part of the rack, but we cannot say which is the maximum T expected), we can't consider this point as our case.
d) The estimated pressure rise from thermal expansion is within the design limits of the equipment or piping.
I used the equation (3) from API 521 (6th edition, 2014) section 4.4.12.4 for pressure rise due to simultaneous heating of the pipe and blocked-in liquid and I am getting a pressure rise of 49 kg/cm2 by the increase of 1ºC of temperature.
I also calculate the temperature rise due to solar radiation (taking 1.04kW/m2 for intensity of solar radiation in accordance with API 521) and I am getting a temperature rise of 5ºC, resulting in a pressure increase of 245 kg/cm2 based on the results of pressure increase I mention previously.
This does not make much sense so I am wondering if this is correct.
Does anyone have any thoughts?