Pressure tank in fire booster pump

Status
Not open for further replies.

Alireza01

Mechanical
Feb 14, 2017
14
Hi
Is That permissible in nfpa 20, to have a pressure tank in addition to pressure maintenance (Jockey) Pump for compensating system leakages ?
 
Replies continue below

Recommended for you

Sure as long as you have a jockey pump you meet NFPA 20. In my mind the pressure tank is just an added thing, really not needed, but if you want it go ahead. Unless you have underground mains on the discharge side of the pump, the jockey should rarely activate unless a main drain is not closed all the way.

 
Why are you proposing a pressure tank?

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
 