PRESSURE TEST ON BOILERS

Status
Not open for further replies.

falco

Industrial
Jul 4, 2001
24
Hey there, Just on equestion, When performing pressure test on a water tube steam boiler, is there any recomendation about the rate pressure should be increased until reached the test pressure I mean how many Psi we must increase per minute untiel we reach the pressure requeired?
best regards!
 
Replies continue below

Recommended for you

falco,
Agree with metengr that there is not minimum rate required for pressure increase per minute for a boiler test. If the pressure does not seem to increase quickly, while pumping into boiler at a good flow, then there could probably be air that has not been vented from the boiler. Maximum pressure increase rates would follow from safe practices. Pressure increase by stages, 25%-50%, would allow time for catching gross leaks. Putting full BFW pressure suddenly on filled boiler might pop pressure relief valves.
 
Break the pressure increase into stages say 25% 50% 75% 90% 100% - and hold for a short time at preceding stages to check for pressure drop.

Cheers
Rob
 