I am a electrician and work in a Hospital . I have studied instrumentation but have a small amount of experience in the field and need some help in choosing a pressure transmitter for a steam boiler . The current situation is a gas steam boiler that operates at 800 Kpa the engineer has asked for the PID controller BTC9090 4-20ma input and output, to modulate the pressure over the range of 850 Kpa to 750 Kpa or better. The current pressure sensor used for the input to the controller is a GEMS 2000BGB1601A10A which has a range of 0-16 Bar and 4-20 ma with a accuracy of approx. 1% . I think this pressure sensor is not suitable .
The range of control desired is 100 Kpa so the pressure sensor will have a output of 1 ma over the 100 Kpa range . The pressure sensor's accuracy of 1% over 16 Bar would give a resolution approx. 6.25 over a range of 100 Kpa .
I thing this is not good enough for good PID control .
Is there a pressure gauge that can withstand a pressure range of approx. 0-10 bar but have a 4-20 ma output when the pressure is in the range of approx. 700Kpa to 900kpa
This would give the controller input greater resolution and hopefully better control.
The other pressure transducer that may work is one with an adjustable span , but I am not sure they exist .
I an not going to be the one to make the modifications to the steam boiler because of safety regulations etc. but I am looking for info to make sure the contractors doe it right .
Any advise on the above would be appreciated.
Best Regards
qwerty2
The range of control desired is 100 Kpa so the pressure sensor will have a output of 1 ma over the 100 Kpa range . The pressure sensor's accuracy of 1% over 16 Bar would give a resolution approx. 6.25 over a range of 100 Kpa .
I thing this is not good enough for good PID control .
Is there a pressure gauge that can withstand a pressure range of approx. 0-10 bar but have a 4-20 ma output when the pressure is in the range of approx. 700Kpa to 900kpa
This would give the controller input greater resolution and hopefully better control.
The other pressure transducer that may work is one with an adjustable span , but I am not sure they exist .
I an not going to be the one to make the modifications to the steam boiler because of safety regulations etc. but I am looking for info to make sure the contractors doe it right .
Any advise on the above would be appreciated.
Best Regards
qwerty2