Preventative Maintenance for Bettis D-Series Rack & Pinion Pneumatic Actuator

Status
Not open for further replies.

Mattpdrexel

Chemical
Dec 20, 2012
3
Hi all,

What would be the appropriate preventative maintenance plan for a D-Series Rack & Pinion Pneumatic Actuator? The actuator operates in mild service conditions and has acted reliably for the past ten years. I do not have much industrial experience, so I have no basis for selecting a maintenance plan for pneumatic actuators.

See attachment for actuator details.

Thanks!

 
Replies continue below

Recommended for you

My opinion is that you should not open an actuator of this type unless it is necessary. There is a greater chance of damaging anything than prolong the life of the actuator.
A visual inspection and functional test shall be a sufficient maintenance. The frequency of maintenance should be driven by the criticality of the valve
 
Thost,

Thanks for the validation, I was heading in that direction. Will be removing the preventative maintenance task now, make the maintenance guys happy.
 
To support Mattpdrexcel (totally agree):

This type of actuators will generally operate a great number of times without failure. On the other hand a long stop-time could wear as much as a very high frequency of repetitive operations.

Main failure components:
Solenoids (not actuator)
Leakage over piston sealings (Test for leakage with solenoid(s) demounted.)
Excessive wear(seldom)
Actuator itself (torque) selected too small.

Main failure causes:
Dirt, water and excessive oil in air (most modern pneumatic systems are oilfree), condensation in air.
Maladjustment (end-stops of actuator), loose or unfit connections to valve.
High voltage peaks to solenoids.
Valve wearing gives higher torque over time.

Preventive by installation: Recheck and improve pneumatic system with all necessary components (water and dirt filters, draining), control correct mounting and el. and mechanical operation and adjustment of complete installation.
During operation: None, check correct operation at the the total systems check intervals.
By failure: replace complete valve and actuator. Often not economical to repair.

Good luck!

 