Good point, but in all honesty (in my case) primary and backup is a catch all term for both identical fully functional A and B relaying (like 2 SEL421s per bay) in addition to scenarios like a main relay with a last resort limited protection backup (like a SEL387 and an SEL501 backup) for a 35kv to 12kv transformer.
It generally wouldn't have the same 'instantaneous' tripping ability as the Primary system.
Well, that can vary by application. Above 35kv (for me anyway) its generally not the speed or protection quality itself sacrificed, rather the "superfluous" abilities of the second relay. For example: very short line spans (like substation to generator) might have something like an SEL311L and with an SEL387L or a typical 115kv line might have an SEL311C with an SEL321. Both provide instantaneous tripping, and both the 311C and 321 may have POTT or DTT, however one relay (backup) is not capable or not set to perform functions such as auto-reclosing, event data recording, control of MODs, ect, ect, ect. The idea is that protection needs come first, and unless other functions are absolutely essential beyond that; a much cheaper, function limited secondary (backup) relay is used.
On things like 345kv and above, the general design idea is having having everything identically replicated with any relay having the full ability of the other. To sum it up 3 types of primary and back exist for me:
Level 1. Full protection primary relay with an essential protection limited backup (such as transformer differential, neutral over current, buckholtz, overtemp, ect A; over current 50/51 only B). Typical for 12 to 66kv systems.
Level 2. Full spectrum protection only for both primary and secondary relaying, with secondary having no burden beyond protection. (such as a 115kv transmission line where both A and B posses identical step distance, POTT, 87, ect; however B does not provide anything beyond that like auto reclosing) Typical for 69kv to 230kv
Level 3. Full protection, monitoring, recording and control capabilities for both A and B relays. Any can do the full work of the other no limitations. Often done via 2 identical relays. Typical for 345kv and over.
However, thats not to say Level 3 is like Level 1 or 2, even though every application gets called primary and backup.