Just a line to let you all know the Marina finally found the source of this intermittent problem.
The brackets had failed( Rusted out) on a conduit allowing it to touch the water. A small amount of seawater had leaked in and traveled along the conduit until it reached an area where it could cause a current leakage. This got to be enough to where it would boil the water in the conduit dry, but not enough to trip the main breaker. Once the water boiled out the problem went away until more water leaked back in. Over a period of time it got worse to where there was finaly enough current to trip the breaker.
B.E.
The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them. Old professor
Just a line to let you all know the Marina finally found the source of this intermittent problem.
The brackets had failed( Rusted out) on a conduit allowing it to touch the water. A small amount of seawater had leaked in and traveled along the conduit until it reached an area where it could cause a current leakage. This got to be enough to where it would boil the water in the conduit dry, but not enough to trip the main breaker. Once the water boiled out the problem went away until more water leaked back in. Over a period of time it got worse to where there was finaly enough current to trip the breaker.