Problem with SR489 Multilin 1

Status
Not open for further replies.

Ealberto

Electrical
Jun 28, 2005
1
Hi everybody, I'm getting a problem with one SR489 Multilin, one of its analog output sudently change signal level, This refers to MVAR, and is calibrated to:
4mA=-3.37MVAR to 20mA=3.37MVAR. At normal power factor it got 0.9MVAR but sudently it increased to maximum setting (3.37MVAR). I did changed the input analog module on PLC in order to eliminate this posibility. I see the problem is with SR489 relay. What can I do, in order to fix it? Thanks for your help.
Ealberto
 
Replies continue below

Recommended for you

If you set 4mA AND 20 mA equal to 3.37 MVAR, that's pretty much what you're going to be reading. I assume the 4mA should be set to either 0 or -3.37 MVAR. If the MW and MVAR are reading correctly on the meter, problems with the analog output must be related to the scaling factors, a wiring problem or a hardware problem in the 489. I'd suggest putting a 1 ohm or similar precision resistor in series with the 4-20mA and checking the voltage. This will enable you to determine the current output from the 4-20mA.

Don't forget that the MVAR can be positive or negative.
 
Hi dpc,

4mA=-3.37MVAR

There's a '-' symbol there. I didn't spot it either at first read. Agree with the rest. I'll enquire whether we've had anything similar with our Multilins.


----------------------------------

If we learn from our mistakes,
I'm getting a great education!
 
Sorry, I missed the minus sign. My bad.
 