- 86
I have a difficult problem. Liquid propane is sent to two pipelines or a tanker truck rack. The suction pipeline to the pumps is uninsulated. There is no pressure control on the propane bullets. The pumps are fed 5 at a time to a pump through a single 4" sch 80 bottom connection for each bullet. The pipelines are buried except for the one to the truck rack. We have trouble pumping from the bullets as level drops below 45% when the pressure is about 110 psig or lower. The operators seem to think that ambient temperature is the source of their troubles. They have no trouble with the pumps when they operate below 70 F but by mid-afternoon in the spring or summer the pumps can't deliver to the truck rack. The buried pipelines still have trouble below 45% level in the bullets.
I looked at the situation and concluded the following problems after modeling the system with Hysys: 1) As the pressure drops, the saturation temperature rises until mostly vapor is flowing to the pump; 2)If flow can be maintained, the auto-refrigeration from pressure drop partially counteracts the heat transfer to air; 3) The heating of the liquid caused by pumping saturated liquid/vapor through the pump bumps the pipeline temperature up and produces more vapor.
One of the engineers seems to think that one approach to the problem is to change the flow controls at the truck rack. He wants a linear valve in place of an equal % valve and now wants to install 2 smaller valves in split range or sequence (I suggested the later) controlled by a new DP transmitter. I suggested moving the flow orifice upstream of the flow control valve. Hysys doesn't indicate choked flow in the line after the control valve even when I force the pump to the limit on suction vapor content.
I think the heart of this problem is the lack of pressure control on the bullets. There is no pump line back to the bullets. Instead, the operators flare the gas from the pump suction line to a flare.
What do you think? Any ideas?
I looked at the situation and concluded the following problems after modeling the system with Hysys: 1) As the pressure drops, the saturation temperature rises until mostly vapor is flowing to the pump; 2)If flow can be maintained, the auto-refrigeration from pressure drop partially counteracts the heat transfer to air; 3) The heating of the liquid caused by pumping saturated liquid/vapor through the pump bumps the pipeline temperature up and produces more vapor.
One of the engineers seems to think that one approach to the problem is to change the flow controls at the truck rack. He wants a linear valve in place of an equal % valve and now wants to install 2 smaller valves in split range or sequence (I suggested the later) controlled by a new DP transmitter. I suggested moving the flow orifice upstream of the flow control valve. Hysys doesn't indicate choked flow in the line after the control valve even when I force the pump to the limit on suction vapor content.
I think the heart of this problem is the lack of pressure control on the bullets. There is no pump line back to the bullets. Instead, the operators flare the gas from the pump suction line to a flare.