I have worked on a large installation with state of the art software, and compared results with three other, eminent engineering companies. The following do not constitute questions so much as observations of some of the inconsistencies and challenges arising from trying to apply the above guides and codes in a meaningful (not just academic) fashion.
Commentary and dialogue is appreciated. Please reference the following numbered paragraphs or add new numbers for additional concerns.
1) Responsibility is not clearly delineated between the journeyman, his employer or the site owner. This is not a large concern and does not prevent us from applying labels.
2) NFPA 70E prescriptive tables include a range of risk category PPE requirements for identical equipment, depending on how involved the described work will be. It is understood that some weighting factor combined with industry experience has been applied to achieve these results. This mechanism is not available in the calculation methods, and though the principles are understood, the liability of adjusting risk categories apart from the given calculations is more than any firm would choose to use. The result is overprotection that might not be followed. This is a medium concern, but does not prevent us from applying labels, but does hamper administrating a safety plan.
3) IEEE 1584 can generate unlikely results such as quarter mile safe approach distance to a regular 480V transformer. The given remedy is to limit clearing time to 2 seconds. This type of patch calls into question the reliability of the calculation. This is a large concern in the context of item 4 below.
4) IEEE 1884 calculated arc flash exposures do not converge with predictable results. This is acknowledged in NFPA 70E, but no real world solution is suggested. For example, increasing fault current may either reduce or increase exposure depending on many other parameters. These calculations have been defended as the best empirical results available, but that is not good enough, the industry needs to perhaps compromise the results a little bit to make the results predictable or this whole thing remains an unmanageable liability.
For example, we now get differing calculated arc flash exposure based on FUSE manufacturer (of 100E type fuses). It is unreasonable to inventory equipment to that level of detail, yet failure to do so may constitute a liability. Seeing how particular the calculations are, it seems the greatest influence of calculated exposure might be arc resistance itself. This will be influenced on unpredictable atmospheric conditions, yet if the effect is to reduce arc current to just less than instantaneous pick up (many of which are being adjusted to reduce calculated exposure to workable levels) the resulting exposure could soar from Risk Category 1 to “Dangerous Unworkable”. This simple phenomenon seems to blow the whole theory. In discussion I have been told that any analysis and PPE is better than before (true), however; imagine this getting into the hands of an aggressive personal injury lawyer. Am I overlooking something?
I feel the science behind the calculations should be tampered with to achieve consistent predictable results even if not quite as accurate.
Commentary and dialogue is appreciated. Please reference the following numbered paragraphs or add new numbers for additional concerns.
1) Responsibility is not clearly delineated between the journeyman, his employer or the site owner. This is not a large concern and does not prevent us from applying labels.
2) NFPA 70E prescriptive tables include a range of risk category PPE requirements for identical equipment, depending on how involved the described work will be. It is understood that some weighting factor combined with industry experience has been applied to achieve these results. This mechanism is not available in the calculation methods, and though the principles are understood, the liability of adjusting risk categories apart from the given calculations is more than any firm would choose to use. The result is overprotection that might not be followed. This is a medium concern, but does not prevent us from applying labels, but does hamper administrating a safety plan.
3) IEEE 1584 can generate unlikely results such as quarter mile safe approach distance to a regular 480V transformer. The given remedy is to limit clearing time to 2 seconds. This type of patch calls into question the reliability of the calculation. This is a large concern in the context of item 4 below.
4) IEEE 1884 calculated arc flash exposures do not converge with predictable results. This is acknowledged in NFPA 70E, but no real world solution is suggested. For example, increasing fault current may either reduce or increase exposure depending on many other parameters. These calculations have been defended as the best empirical results available, but that is not good enough, the industry needs to perhaps compromise the results a little bit to make the results predictable or this whole thing remains an unmanageable liability.
For example, we now get differing calculated arc flash exposure based on FUSE manufacturer (of 100E type fuses). It is unreasonable to inventory equipment to that level of detail, yet failure to do so may constitute a liability. Seeing how particular the calculations are, it seems the greatest influence of calculated exposure might be arc resistance itself. This will be influenced on unpredictable atmospheric conditions, yet if the effect is to reduce arc current to just less than instantaneous pick up (many of which are being adjusted to reduce calculated exposure to workable levels) the resulting exposure could soar from Risk Category 1 to “Dangerous Unworkable”. This simple phenomenon seems to blow the whole theory. In discussion I have been told that any analysis and PPE is better than before (true), however; imagine this getting into the hands of an aggressive personal injury lawyer. Am I overlooking something?
I feel the science behind the calculations should be tampered with to achieve consistent predictable results even if not quite as accurate.