Propane gas and electrical enclosures.

Status
Not open for further replies.

sloop

Mechanical
Apr 18, 2003
7
I have an application where it is suggested that the LP gas manifold can be placed inside the electrical enclosure with 110vac controls. Is this appropriate? It has also been suggested that a seperator panel (not air tight) between the gas and electrical component would be OK.
 
Replies continue below

Recommended for you

Neither of these concepts are safe. The regulations refer to zoning of gas dangerous areas. The manifold would be considered zone 1 or 2.
The more onerous being zone 1 where gas is likely in normal operation. Zone 2 refers to gas being present only in a fault condition.
In both cases only certified electrical equipment is allowed to be installed in a gas dangerous area. The certification must refer to the gas in question.
The 110vac you refer to is definitely an ingnition source and should be either located in an Ex certified enclosure (refer IEC 60079), or outside the gas area.
This is risky and specialist stuff. If your installation causes an explosion you will be guilty under the Health and Safety Act.



 