Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

proper chilled water pump sizing

Status
Not open for further replies.

duvy

Mechanical
May 7, 2008
3
When a system requires a GPM flow rate to supply system AHUs is there a percentage increase needed to over come pipe resistance? If system GPM is 172 needed to AHUs, should the pump chosen be rated at 172GPM or increased by a certain percentage say 25%,215 GPM to insure enough GPM for the chilled water system.
 
Replies continue below

Recommended for you

Negative. The pump should be sized for the calculated flow rate and calculated head loss. Select the pump in the middle of the pump curve, so that you will have some "wriggle room" in case your calculations are off or the operating conditions change (additional load). Flow friction increases by Q^1.85, so you do not increase flow to overcome friction. You increase Hp instead.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor