Dear friends!
Two Power transformers each having 50 MVA/ 33/11 kV/ Dyn11/ OLTC, are going to be connected in Double Ended configuration ( i.e. each 11 kV secondary is connected to Bus A & Bus B having a NO Bus-Tie ) to a 11 kV switchgear. They are going to be fed from a remote 33 kV substation about 850 m away. Each of these 850 m long 33 kV cables are going to be directly terminated to the 33 kV side of each transformer without an additional 33 kV switchgear. The protective relay scheme for this Feeder & Transformer has got two different options.
Option #1: Feeder and Transformer as two Zones of protection.
First zone covers the 33 kV feeder with Overcurrent (50/51),Earth Fault (51N) & Sensitive Ground Fault (50GS) protection extending from the 33 kV SF6 breaker up to the primary Delta winding of the transformer, which is typical for a transformer feeder.
Second zone covers the 50 MVA transformer as a unit with Phase Differential (87T) and Restricted Earth Fault (87N) protection, also typical unit protection for a large power transformer.
Option #2: Feeder and Transformer as single Zone of protection.
This consists of Overcurrent (50/51), Earth fault (51N) & Sensitive Ground fault (50GS) for the feeder, Phase Differential (87) for the feeder plus transformer and Restricted Earth Fault (87N) protection, a typical “Translay Differential Scheme “ (similar to a conventional Phase Differential protection for a MV cable+motor )
As far as better coordination, cost, c/t locations, feeder length etc are concerned I always support the option 1. On the other hand some of our friends may already be using the option 2 ( if I am not mistaken it is the so called Translay scheme) in the field and may (or may not) support the same. Therefore I welcome your comments (pros & cons) on these two options.
Thanks in advance!
Two Power transformers each having 50 MVA/ 33/11 kV/ Dyn11/ OLTC, are going to be connected in Double Ended configuration ( i.e. each 11 kV secondary is connected to Bus A & Bus B having a NO Bus-Tie ) to a 11 kV switchgear. They are going to be fed from a remote 33 kV substation about 850 m away. Each of these 850 m long 33 kV cables are going to be directly terminated to the 33 kV side of each transformer without an additional 33 kV switchgear. The protective relay scheme for this Feeder & Transformer has got two different options.
Option #1: Feeder and Transformer as two Zones of protection.
First zone covers the 33 kV feeder with Overcurrent (50/51),Earth Fault (51N) & Sensitive Ground Fault (50GS) protection extending from the 33 kV SF6 breaker up to the primary Delta winding of the transformer, which is typical for a transformer feeder.
Second zone covers the 50 MVA transformer as a unit with Phase Differential (87T) and Restricted Earth Fault (87N) protection, also typical unit protection for a large power transformer.
Option #2: Feeder and Transformer as single Zone of protection.
This consists of Overcurrent (50/51), Earth fault (51N) & Sensitive Ground fault (50GS) for the feeder, Phase Differential (87) for the feeder plus transformer and Restricted Earth Fault (87N) protection, a typical “Translay Differential Scheme “ (similar to a conventional Phase Differential protection for a MV cable+motor )
As far as better coordination, cost, c/t locations, feeder length etc are concerned I always support the option 1. On the other hand some of our friends may already be using the option 2 ( if I am not mistaken it is the so called Translay scheme) in the field and may (or may not) support the same. Therefore I welcome your comments (pros & cons) on these two options.
Thanks in advance!