protecting ups from back emf when using as an inverter

Status
Not open for further replies.

vortexwizard

Mechanical
Jan 13, 2019
3
Hi i use old ups(uninterupted power supplies) the type used in offices made by APC with larger battery banks for very cheap off grid inverters, one problem with this i have read is the damage caused by back emf caused when a motor stops. How is it best to protect against this?
Many thanks
 
Replies continue below

Recommended for you

I think there is something missing or wrong in your basic premise. If you are talking about an AC induction motor, "stopping" is generally done by opening a contactor, so there would be no back EMF issues at all.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
hi it is just what i have read, i am mainly using them with power tools and a water pump, so you think there will be no problem with this? I am not using any contactors just the inbuilt trigger switches on power tools and unplugging the water pump to turn it off, if i were to turn off the power at the ups(inverter) would that be a problem? I think as they are designed to run computers and not inductive loads there maybe some additional protection missing or are people over worrying? I am mainly using the older grey apc smart ups series. Maybe back emf is the wrong terminology but what i am refering to is the current surge when the induction motor is switched off.
Many thanks for reply, i hope i am being clear :)
 
More likely a voltage disturbance caused by the arcing at the contactor as it interrupts an inductive load. Most UPS designs won't be particularly happy with that type of load.
 
thanks, so is there any circuitry i can add to minimise this like the equivalent of a snubber circuit and how do normal inverters deal with this? Thanks
 
Inverters don't like AC motors as a general rule, but it depends on how much bigger the inverter is than the motor in question. But portable power tools usually use "Universal" motors, a DC motor designed to accept AC input. They don't have the same sort of inrush current profile of an induction motor.

I have started a 5HP 230V 3 phase induction motor for an A/C unit on the output of a double conversion UPS, but the UPS was 25kVA with maybe 10kVA of total load on it.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 