mgtrp
Electrical
- May 4, 2008
- 326
I'm looking for opinions on the location of protection CTs for small medium-voltage generators (800-1200 kW) that do not use differential (just overcurrent).
Some people prefer them to be mounted on the neutral end of the generator winding, so that they can measure the generator contribution to internal faults. This seems reasonable—a set of grounds left on after maintenance would be quite the fireball otherwise, especially with a PMG-fed unit.
Others prefer them to be mounted on the phase end of the generator winding, so that they measure the system contribution to internal faults. This also seems reasonable—the fault can be cleared much faster (trip instantaneously), and coordination with other units on the same bus is possible. It also allows for current-based ground fault protection of high-impedance or ungrounded generators based on utility contribution. I also note that this seems to be the more typical arrangement of small diesel genset manufacturers.
Any thoughts as to which is preferable? Would operating regime make a difference (units that are run for extended periods vs started and stopped more often)?
Thanks in advance,
mgtrp
Some people prefer them to be mounted on the neutral end of the generator winding, so that they can measure the generator contribution to internal faults. This seems reasonable—a set of grounds left on after maintenance would be quite the fireball otherwise, especially with a PMG-fed unit.
Others prefer them to be mounted on the phase end of the generator winding, so that they measure the system contribution to internal faults. This also seems reasonable—the fault can be cleared much faster (trip instantaneously), and coordination with other units on the same bus is possible. It also allows for current-based ground fault protection of high-impedance or ungrounded generators based on utility contribution. I also note that this seems to be the more typical arrangement of small diesel genset manufacturers.
Any thoughts as to which is preferable? Would operating regime make a difference (units that are run for extended periods vs started and stopped more often)?
Thanks in advance,
mgtrp