Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations The Obturator on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

protection curve but only a point (overcurent 51)

Status
Not open for further replies.

godel123

Petroleum
Jun 10, 2011
51
hi
overcurrent (51) protection.
When we see 100 A 0.3 s.
so why we talk about curve, but there is only a point
 
Replies continue below

Recommended for you

At 100 A you see 0.3 s. If you test the relay at 150 A, it will operate faster. With lower current the operate time will be lower. That is the reson why we talk about curve (inverse, extremely inverse and so on) in contrast with the definite time overcurrent protection (50) where the operate time is fixed and does not depend on current level.
 
how to "choose" the seting values to protect a motor, i mean is there a genral considerations or we have to make calculations?
exemple of a motor : 50 Kw, 400 V.
 
For a 50kW 400V motor just buy an overload relay to suit the motor full-load current. Normally a Class 10 overload is fine. If it is a load with unusually severe starting conditions, and if the motor is designed to cope with it, then you might look at a Class 20 or even a Class 30 overload. I've never come across a Class 30 relay in real life, even on conveyor duty, but they exist in catalogues. Standard IEC motors simply won't survive a Class 30 start, it would have to be a 'special'.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor