rockman7892
Electrical
- Apr 7, 2008
- 1,161
I wanted to hear the approach that others take when settings adjustable LV molded case breaekrs in order to protect LV 480V generators. I have always been told that the breaker should be set so that the breaker curve falls below the generator damage point on the TCC and so that the breaker short time range crosses the generators decrement curve at some point. The damage curve and decrement curve that I am refering to are the ones created automatically be commercial sofware such as SKM, etc.. depending on generator size and other paramaters.
Does anyone have a specific methodology or reference to how these breakers should be set in order to protect generator and allow in most cases selective coordination with downstream breakers. Do most people use the decrement curve and damage point created by commercial software, or do they build custom damage curves and decrement curves based of generator datasheets?
Does anyone have a specific methodology or reference to how these breakers should be set in order to protect generator and allow in most cases selective coordination with downstream breakers. Do most people use the decrement curve and damage point created by commercial software, or do they build custom damage curves and decrement curves based of generator datasheets?