jkampana
Mechanical
- Aug 2, 2011
- 45
I am doing NFPA 13 system in a senior housing project. The living quarters are a residential light hazard occupancy. I want to make sure I am designing these rooms correctly.
The heating ducts will be ran below the floor joists then box around creating a soffit on one side of the room. In the main living room the soffit 15" wide x 24" deep. another is 33" x 12" and another 15" x 12". If I am reading NFPA correctly I will have to have a pendent sprinkler installed under that soffit if it projects away for the wall more than 8"(8.10.7.1.5.1)? Is this correct and if not would I use figure 8.10.6.1.2(b) for the soffits under 30" wide? What then is the ruling for soffits wider than 30"?
Thanks in Advance.
The heating ducts will be ran below the floor joists then box around creating a soffit on one side of the room. In the main living room the soffit 15" wide x 24" deep. another is 33" x 12" and another 15" x 12". If I am reading NFPA correctly I will have to have a pendent sprinkler installed under that soffit if it projects away for the wall more than 8"(8.10.7.1.5.1)? Is this correct and if not would I use figure 8.10.6.1.2(b) for the soffits under 30" wide? What then is the ruling for soffits wider than 30"?
Thanks in Advance.