Pete2
Electrical
- Jan 24, 2001
- 3
We are designing a service entrance to a sewage treatment plant in Souther California. Power from the utility's 2000/2576 kva transformer enters at 480 volts through a 3200 amp main circuit breaker. Back-up power is from a 1500kw diesel generator through a 2500 amp circuit breaker to the main switchgear bus.
The circuit breakers are electrically operated and controlled by an automatic throw-over control system in the switchgear. Trouble is detected on the line side of the main breaker by devices 27, 47, 59, and 81 O/U (undervoltage, neg. sequence voltage, overvoltage, and frequency relays).
A comment from the client states that relays 59, 47 and 81 are not required for sensing availability of normal power. In fact they may interfere with our attempts to load shed at the generator bus level with frequency relays, they say.
I don't understand how relays 59, 47 and 81 on the incoming line will interfere with generator load shedding. Can anyone shed some light on this issue?
The circuit breakers are electrically operated and controlled by an automatic throw-over control system in the switchgear. Trouble is detected on the line side of the main breaker by devices 27, 47, 59, and 81 O/U (undervoltage, neg. sequence voltage, overvoltage, and frequency relays).
A comment from the client states that relays 59, 47 and 81 are not required for sensing availability of normal power. In fact they may interfere with our attempts to load shed at the generator bus level with frequency relays, they say.
I don't understand how relays 59, 47 and 81 on the incoming line will interfere with generator load shedding. Can anyone shed some light on this issue?