Dear Mr. CuriousElectron
Q. "... I need to check that an existing dry-type 100kVA transformer .... is fit for duty. What kind of tests should I run apart from performing the visual inspection?"
A. some basic procedures:
a) [vacuum] instead of [blowing off] the dust as it will be disperse into the space and deposit on other equipments. Dry cleaning the windings and insulators if any,
b) visual inspection for any cracks, damaged insulation, corrosions and torque all connections,
c) insulation resistance test with 500Vdc: pri-frame, sec-frame and pri-sec . For rated voltage < 1kV , the insulation resistance shall > 1M Ohm. If lower, heat up with heater lamps or by short-circuit circuiting current with low voltage,
d) high-voltage test with AC voltage at [2 x rated voltage + 1000V] between pri-frame, sec-frame and pri-sec. There shall be [no break-down] for a duration of [one minute]. Ignore the value of leakage currents. There is some defects if the leakage current > the max setting of the test set!,
e) temporally connect a single-phase/three-phase (low voltage) supply to the [high-voltage] terminals. Measure the voltage at the [low-voltage] terminals. Check that the [voltage ratio] is as per the name-plate rating,
f) for a 100kVA transformer, it "may?" (not) required to conduct the [Capacitance and tan delta test], as the test set cost and the lobour charges would not justify it.
Che Kuan Yau (Singapore)