PRV at Tank and at Pump Centrifugal

Status
Not open for further replies.

TengkuSyahdilan

Mechanical
Sep 25, 2008
17
I have a pipeline system running from berth to tank and pipeline from tank to pump centrifugal (See the attachment). my question are why the inlet piping at tank need a PRV? and why the outlet doesn't need it? And why in the centrifugal pump we must install PRV too from discharge to suction like you in the P&ID at the attachment. All i know that PRV is at the roof of the tank and usually is Reciprocating pump that use a system PRV like this....am i correct?
But the client want that no PRV at the roof of the tank but it must be at the inlet line. and for line in the pump room the client insist to use PRV in this centifugal pump. The design pressure is 100 PSi with temperature 45 C. the pipe size is 6 inch sch 40. The pumpis design for flow rate 150 m3/h.
Can someone explain about this PRV case?

Regards


T.Syahdilan
 
Replies continue below

Recommended for you

Please put your drawing in a common format, pdf, png, jpg etc.

What type of tank is this?

If I understand your system explanation,
There is obviously a pressure limit on the tank and the inlet line can possibly reach a higher pressure when it is being filled by the ships.

There is not a PRV on the tank outlet, because there is no hi pressure source inside the tank, only fluid level head pressure.

PRV on the recycle line is to prevent discharge pressure from reaching the suction line, pump suction flange and from keeping hi pressure fluid from backflowing into the tank.

Don't forget to reload the diagram.

**********************
"Pumping accounts for 20% of the world’s energy used by electric motors and 25% to 50% of the total electrical energy usage in certain industrial facilities." - DOE statistic (Note: Make that 99.99% for pipeline companies)
 
The PRV at the tank is for thermal expansion IF the block valve is closed at the tank and also at the main header. It would then relieve into the tank to guard against over pressurizing that piping system.
The PRV at the pumps is to protect the discharge piping if the pump tried to over pressurize the system, discharging back to the suction side.
Two problems I see with your dwg. First the check valves at the tank are backwards! Also the PRV's at the pumps are backwards too. They should discharge to the suction side not to the discharge side. Also be sure to Lock-Open or Car Seal Open the block valve under the PRV's.
...My $0.02, Good Luck! ...Mark
 
Looking at the diagram my guess is that all of the PSVs are for thermal expansion: 1" PSV on a 6" line to handle thermal expansion of liquid if the line from the barge is left full after loading, and potential thermal expansion in the pump suction lines if those are left full. On a side note, I'm assuming that the check valves on the tank inlet piping are shown backwards, and that the nozzle in the tank is the fill line. Not sure where this is located, but in the US the coast Guard requires barge pumps to have a PSV installed that lifts at 125 psig, so that the barge pump doesn't overpressurize the piping system. Overpressure prtoection on the tank itself is a different scenario, and may or may not need to be provided based on the potential overpressure scenarios and ratings of the tank.
 