Hi,
I am curious as to the experience of others in using multifunction testers (primarily designed for insulation resistance measurements) for measuring prospective short-circuit currents with regards to accuracy.
Typically in my company we use the Megger range of MFT (such as MFT-1835) to measure the short-circuit currents on the LV terminals of a new transformer or main switchboard installation.
Recently I have noticed the measured values to be significantly deviated from the theoretical short-circuit current used in the design (design including HV impedances) by upto 50%. This is at the point where it gives me concerns as to the adequacy of the HV protection to operate in all scenarios on a fault between the LV terminals an the first LV protective device.
Can anyone shed any light on similar experiences or recommendation to use a dedicated test unit (I'm not aware of what dedicated units might be used)?
Thanks
I am curious as to the experience of others in using multifunction testers (primarily designed for insulation resistance measurements) for measuring prospective short-circuit currents with regards to accuracy.
Typically in my company we use the Megger range of MFT (such as MFT-1835) to measure the short-circuit currents on the LV terminals of a new transformer or main switchboard installation.
Recently I have noticed the measured values to be significantly deviated from the theoretical short-circuit current used in the design (design including HV impedances) by upto 50%. This is at the point where it gives me concerns as to the adequacy of the HV protection to operate in all scenarios on a fault between the LV terminals an the first LV protective device.
Can anyone shed any light on similar experiences or recommendation to use a dedicated test unit (I'm not aware of what dedicated units might be used)?
Thanks