NFPA 14 (2000ed) Chapter 5-7(1) Exception No. 1 allows the AHJ to permit a hydraulically calculated standpipe to provide 65PSI at the top (rather than 100psi). Fine.
BUT... Exception No. 2 starts off: In other than high rise buildings...
Does anyone know why Exception No. 1 would NOT be allowed in high rise buildings??
Especially since, in a large city with full-time personel and pumper trucks, the Fire Department will pressurize the (in this case a class I) standpipe to whatever they want anyway. It almost makes the PSI at the top redundant because a class I standpipe is for F.D. use only anyway.
Any thoughts??
BUT... Exception No. 2 starts off: In other than high rise buildings...
Does anyone know why Exception No. 1 would NOT be allowed in high rise buildings??
Especially since, in a large city with full-time personel and pumper trucks, the Fire Department will pressurize the (in this case a class I) standpipe to whatever they want anyway. It almost makes the PSI at the top redundant because a class I standpipe is for F.D. use only anyway.