Since I'm completely new to PSS/E I have a following question about the output of this file.
I am analyzing a smaller network that is connected to a larger network through a transformer.
A short circuit analysis is made on the bus of the larger network (meaning, I need the equivalent impedance of it to calculate short circuits in the smaller network). Consider the following output from PSS/E:

SS®E ASCC SHORT CIRCUIT CURRENTS THU, MAY 19 2011 14:52
X---------- BUS ----------X
MVA AMP DEG
3PH 2912.16 7310.2 -54.88
LG 3005.43 7544.3 -54.45
THEVENIN IMPEDANCE, X/R (OHM) Z+:/18.457/82.188, 7.28914 Z-:/18.258/82.622, 7.72320 Z0:/16.944/80.360, 5.88722

How do I read the thevenin impedances, because it seems that either R is too large, or I am reading it completely wrong. For example, is the positive sequence X+=18.457 and positive sequence Z+=7.28 ?
The "correct" impedances will be then have to be trasformed to a lower voltage level. But what are the correct values?
Thanks in advance!
(And no, this is not an april joke!)
 
Replies continue below

Recommended for you

Not knowing PSEE (I use ASPEN), I would guess Magnitude/Angle, X/R, for each of the three sequences.

 