Hopefully a relatively simple question, but struggling to find answers in the relevant standards (API/ISO etc.,)
My question concerns conventional spring loaded pressure relief valves. Typically for gas, relief valve blowdown will be around 7% and for liquid about 20%.
If the safety valve does not fully lift in a relief event and begins to close after the event is over, will the pressure at the relief valve still need to decrease to below the blowdown for the valve to reseat?
For example, if I have a liquid relief valve set at 10 barG, and I have a relief event which results in the safety valve only partially open, and the normal operating pressure in the line is 9 barG - will this mean the safety valve will not reseat and continue to simmer/leak?
Thanks