txplpro
Mechanical
- Jun 25, 2015
- 3
My company is reviewing a client's application for adding a new 36" 760kbpd ASME Class 600 crude pipeline to an existing Class 150 B31.4 tank terminal. The client, the terminal owner/operator wants our engineering company to accept their design as-is with a PSV installed 1600 linear feet away downstream of the new PCV. The specification break is at the first manual block valve 20 ft downstream of the PCV. There are additional manual isolation valves between the PCV and PSV, all locked open, according to the client. If the PCV fails open or at too high a pressure above setpoint, the terminal piping can be overpressured.
I called this into question as there is too much distance between the PCV and PSV. I would rather see the PSV installed as close as possible to the first blockvalve / specification break.
Does anyone agree that the PSV is close enough at 1600' away? Why?
Facts of interest-
Client's design is at 60% review stage. A HAZOP was done by others, without my co. participating.
The PSV sizing was done before this project began. The client 'feels' it is adequate as to location and relieving capacity. It is located in Class 300 piping, but the piping between the PCV and PSV is Class 150. I don't know what the setpoint is.
The client is an international major like (Exxon, Chevron, Enbridge, or one like them).
The clients own standards prohibit doing what they are planning to do.
-locate PSV as close as possible to the spec. break (not 1600' away)
-overpressure protection must be automatic and continuous (not dependent on operator intervention)
-Terminal piping downstream of the pipeline discharge must be Class 300 minimum (not Class 150)
Many thanks and regards. I use this forum frequently.
I called this into question as there is too much distance between the PCV and PSV. I would rather see the PSV installed as close as possible to the first blockvalve / specification break.
Does anyone agree that the PSV is close enough at 1600' away? Why?
Facts of interest-
Client's design is at 60% review stage. A HAZOP was done by others, without my co. participating.
The PSV sizing was done before this project began. The client 'feels' it is adequate as to location and relieving capacity. It is located in Class 300 piping, but the piping between the PCV and PSV is Class 150. I don't know what the setpoint is.
The client is an international major like (Exxon, Chevron, Enbridge, or one like them).
The clients own standards prohibit doing what they are planning to do.
-locate PSV as close as possible to the spec. break (not 1600' away)
-overpressure protection must be automatic and continuous (not dependent on operator intervention)
-Terminal piping downstream of the pipeline discharge must be Class 300 minimum (not Class 150)
Many thanks and regards. I use this forum frequently.