Is there any difference between a Pressure Safety Valve and a Safety Relief Valve?

or are these just 2 names for the same valve?

if there are differences, what are they please?

Thanks,

Matt.
 
Replies continue below

Recommended for you

Hello Matt,

- A Safety Relief Valve (SRV) will (automatically) open in case of too high upstream pressure. And relief the excess pressure.
- An Emergency Shutdown Valve (ESD) will close in case of an emergency like a high pressure. And block the high upstream pressure.
- A Pressure Safety Valve (PSV) can be both. However be carefull! PSV is also often used for Pressure Shutdown Valve. Which will be the closing type again.

Good luck!
Terje

 
Time to review a bunch of ASME terms such as Safety Valve and Safety Relief Valve for steam and boiler applications as well as other terms for unfired pressure vessels. This can be a lengthy review.
A. Safety Valves. A safety valve is an automatic pressure relieving device actuated by the pressure generated within the boiler and characterized by full-opening pop action. It is used for steam service. Valves are of the spring-loaded pop type and are factory set and sealed.

B. Safety Relief Valves. A safety relief valve is an automatic pressure relieving device actuated by the pressure generated within the boiler. It is used primarily on water boilers. Valves of this type are spring loaded without full-opening pop action and have a factory set nonadjustable pressure setting.

In UG-126 the first sentences state “(a) Safety, safety relief, and relief valves shall be of the
direct spring loaded type.
(b) Pilot operated pressure relief valves may be used, provided that the pilot is self-actuated and the main valve will open automatically at not over the set pressure and will discharge its full rated capacity if some essential part of the pilot should fail.

For process equipment use ASME PTC 25 for the pressure relief device definitions.
...
 
I agree with the definitions for Safety Relief Valve for ASME Sec. IV, Heating Boiler Service. However, Sec. VIII SRV may be in any number of services and may include fixed blowdown diesign or Pilot Operated Valve as well as adjustable blowdown design, conventional spring loaded valves (i.e. Crosby JOS, Dresser 1900, Farris 2600, all are API Standard Process SRV). However, in many plants, PSV simply indocates Plant Safety Valve on a P&ID which may actually be a Safety Valve, Safety Relief Valve or Relief Valve. All three are seperate sub-divisions of Pressure Relief Valves (see PTC 25-2001 for definitions). Basically a Safety Valve is typically Open Yoke (exposed spring), two ring design (adjustable blowdown) for compressible (primarily steam) service. Relief Valves are typicslly non-code applications (pump discharge, thermal relief) with closed bonnet, no adjusting ring, for incompressible (liquid) service. Safety-Relief Valves have a closed bonnet, one adjusting ring (typical) and are certified for use on Steam, Air/Gas or Liquid. Hence the name Safety-Relief Valve. It will pop on gas (like a safety valve) or open gradually on liquid (like a relief valve) depending on the system where it is installed.

JAC
 
I have always understood a Safety valve to be a Section 1 valve; i.e. Boiler (Fired Pressure Vessel) . 3% overpressure, spring-loaded, adjustable pop and blowdown ring. Manual lifting gear mandated, but really scary to think about using. Usually has an open spring.

A Safety-relief valve is a Section VIII valve: Unfired pressure vessel. 10% OP (16% for combination valves, 21% for fire). Can be Spring, Pilot, Rupture disc, Breaking pin. Steam, Gas, Liquid. Manual lifting gear mandated for steam, air, water at over 140F. Bonnet is usually closed/vented.
 
I agree with Jim Casey. Sec. I "V" Stamp has two exceptions, Part PVG for Vapor Generator has SRV with no lever in "V" Stamp Service and High Temp Water Boiler (>250F or 160 psi) these require Closed Bonnet with Packed Lever, see ASME Sec. I, PG-67.5 Last paragraph.

JAC
 
Or simply (as per cheresources.com)...

SV (or PSV): for compressible fluids

RV (or PRV): for incompressible fluids

SRV: general name for both previous types

Small people talk about others, average people talk about things, smart people talk about ideas and legends never talk.
 
Or more precisly:

Safety relief valve – an automatic pressure relieving device that may be used as either a safety or relief valve, depending on application. A safety relief valve is used to protect personnel and equipment by preventing excessive accumulation.

Safety valve – an automatic pressure relieving device actuated by static pressure upstream of the valve and characterized by rapid full opening or pop action. It is used for gas or vapor service.

Relief valve – an automatic pressure relieving device actuated by static pressure upstream from the valve, which opens in proportion to the increase in pressure over the opening pressure. A relief valve is used primarily for liquid service.