Grounded wye-grounded wye VT connected to an ungrounded system with a secondary fault between phase and neutral in the control wiring. That will produce a certain level of 3V0 that can be detected and may result in the unit being tripped. That can happen for an A-neutral fault, a B-neutral fault, or a C-neutral fault. The secondary must be grounded, exactly once, for safety; so if a grounded neutral carries risk for any phase-neutral fault is there a better approach? That better approach is to ground one phase instead. With all four wires brought to the relay, it can't tell any difference between the two grounding methods for anything that happens on the primary. But on the secondary, the only control wiring fault that can produce 3V0 is a fault between B and neutral. A more secure design without reducing dependability. The biggest potential downside is someone unfamiliar with the scheme coming along later and "fixing" it in the field.