Can someone explain the difference in the Line-Line and Line-Ground ratings for the MV ABB PT in attachment. This datasheet gives model numbers for Line-Line and Line-Ground connected units and I was wondering what the difference is for PT with same primary voltage ratings?
For instance the 2400/4160Y unit is shown under both the L-L and L-G units with the same with the same winding ratio and thus the same 2400V primary voltage rating. Is the only difference here based on the insulation or bushing ratings at the terminals?
I know for pole mounted transformers you can get them for L-G connections where neutral connection is bonded internally to transformer enclosure and thus there is only (1) bushing. Or you can order for L-L connection where transformer has two bushings to be able to connect L-L.
Does anyone know what other manufacturer makes a similar PT as attached besides GE?
Thanks for the help.
For instance the 2400/4160Y unit is shown under both the L-L and L-G units with the same with the same winding ratio and thus the same 2400V primary voltage rating. Is the only difference here based on the insulation or bushing ratings at the terminals?
I know for pole mounted transformers you can get them for L-G connections where neutral connection is bonded internally to transformer enclosure and thus there is only (1) bushing. Or you can order for L-L connection where transformer has two bushings to be able to connect L-L.
Does anyone know what other manufacturer makes a similar PT as attached besides GE?