charz
Electrical
- Jan 11, 2011
- 95
PT: wye grounded - wye grounded.
Ungrounded System.
The secondary of the PT (L1, L2, L3, N) four wires is connected to the Numerical relay. The Numerical relay calculates the zero sequence voltage to detect the ground faults. (No broken delta connection to detect the ground fault). There is no damping resistor at the secondary side.
In our case, the phase- phase voltages are normal, but the phase - neutral voltages are not consistent with each other. Due to inconsistent phase to neutral voltages, the numerical relay operates on ground fault.
1. what happens if the neutral at the Primary of the PT is floated i.e disconnected from ground?
As I understand, In broken delta secondary connection, the relay can not detect ground fault. Will the phase to neutral voltages will be stable? I think no.
2. what happens if the neutral at the secondary of the PT is floated i.e disconnected from ground?
My understanding is that secondary neutral is grounded only for safety point. If secondary neutral is not grounded, can it cause distortion of secondary voltages?
Sometimes the PT secondary fuse gets blown? If there is a short circuit at the secondary loading side, the secondary fuse gets blown. What are other cases the PT secondary fuse gets blown?
Ungrounded System.
The secondary of the PT (L1, L2, L3, N) four wires is connected to the Numerical relay. The Numerical relay calculates the zero sequence voltage to detect the ground faults. (No broken delta connection to detect the ground fault). There is no damping resistor at the secondary side.
In our case, the phase- phase voltages are normal, but the phase - neutral voltages are not consistent with each other. Due to inconsistent phase to neutral voltages, the numerical relay operates on ground fault.
1. what happens if the neutral at the Primary of the PT is floated i.e disconnected from ground?
As I understand, In broken delta secondary connection, the relay can not detect ground fault. Will the phase to neutral voltages will be stable? I think no.
2. what happens if the neutral at the secondary of the PT is floated i.e disconnected from ground?
My understanding is that secondary neutral is grounded only for safety point. If secondary neutral is not grounded, can it cause distortion of secondary voltages?
Sometimes the PT secondary fuse gets blown? If there is a short circuit at the secondary loading side, the secondary fuse gets blown. What are other cases the PT secondary fuse gets blown?