PT shielded cable close to capacitor banks

Status
Not open for further replies.

ePOWEReng

Electrical
Jul 15, 2003
114
Does anybody know a type of PT cable that has a shield that will minimize transients due to magnetic coupling? This is for a sub with cap banks. We tried using a 4 conductor cable with a copper shield but it turns out that doesn't reduce magnetic coupling very well.
 
Replies continue below

Recommended for you

What about using sheilded twisted pair? The shielding needs to be ferrous to shield for magnetic field, I believe.

 
Scottf is right on, you need ferrous shielding for magnetic circuits.

Maybe you could run your wiring in steel conduit.
 

It may be worth investigating if indeed magnetically-coupled capacitor currents are introducing errors in the PT cabling. {As implied, non-ferrous shielding is primarily effective for electrostatic influence.}

If for instance, the PTs are used for capacitor-unbalance protection, some initial or quiescent voltage may be present from accepted capacitor-manufacturing tolerances, and somewhat influence what would be considered an otherwise near-zero secondary quantity, like on the order of a 0.05 per-unit value. The need for sensitivity in ground-overvoltage relaying makes accurate determination of ‘neutral-shift’ voltage quantities important, and otherwise not “buried in the mud.” [Reference IEEE Std C37.99-2000.]
 