Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Pulling Tension Limits for Fulling Grips

Status
Not open for further replies.

nonsinusoidal

Electrical
Mar 28, 2009
81
Does anyone know what is the recommended/Maximum Pulling Tension limits for pulling Concentric neutral, Jacketed, TRXLPE underground cables through conduits? The Underground primary cables are for medium voltages 5kV to 35 kV. In particular, I would like to know the recommended maximum pulling tension limits when pulling one, two, three, four, and parallel TRXLPE, Concentric neutral, Jacketed underground cables? Similarly, I am interested in the maximum pulling tensions for underground 600 volt cables with XLPE Insulation.
 
Replies continue below

Recommended for you

The maximum tension is limited by the cable material, method of attachment of the pulling means, and type and configuration of the raceway. If bends are involved the conduit sidewall pressure may be your limiting factor. There have been several threads here recently on this subject. Some cable manufacturers have helpful installation guides and there are software packages available for these calculations.

Alan
----
"It’s always fun to do the impossible." - Walt Disney
 
Can anyone provide references to information from IEEE or ICC standards which can be helpful to the current methods on how to pull underground cables. In particular, Pulling Underground Cables with Grips attached to the insulation of the cables.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor