Hello,
We made an pullout test (ASTM D3689)on a driven pile with success. The criteria used for the acceptance of the pile is the elastic lengthening + 5mm. I calculated the elastic lengthening with PL/AE, but the bridge engineer says that the elastic lengthening should take into account the soil resistance!? I do not agree with that, but the piles are not accepted until we can give an answer to that, and I do not have arguments. I do not know where to begin either to calculate the ''elastic lengthening'' taking soil resistance into account....
The pile is 14'' diameter pipe pile with 0.375'' wall thickness (356mm x 9.53mm).
Anybody has input to direct me??
Thank you very much in advance.
Jonathan
p.s. You can find the test data joined (in french but it's mostly straightforward)
We made an pullout test (ASTM D3689)on a driven pile with success. The criteria used for the acceptance of the pile is the elastic lengthening + 5mm. I calculated the elastic lengthening with PL/AE, but the bridge engineer says that the elastic lengthening should take into account the soil resistance!? I do not agree with that, but the piles are not accepted until we can give an answer to that, and I do not have arguments. I do not know where to begin either to calculate the ''elastic lengthening'' taking soil resistance into account....