The plant I support has two existing speed controlled simplex diaphragm pump installations (manual stroke adjustment) w/ Coriolis mass meter configured so Flow adjusts stroke speed. Flow has a pulsing frequency of ~ 1sec. Because these are simplex pumps, pulsing affects flow more than 5%, in spite of the pulsation dampener. The second flow is ratio controlled from the first flow.
I would like to take advantage of the constant volume characteristic of the pump to compare the flow generated by the pump to the flow measured by the cmm, as a plausibility check of the health of the cmm and pump. In a sense an on-line prover.
This seems straight forward: stroke speed*volume*cmm density where volume is the calibrated volume @ a stroke setting. However the computed value is in effect a smoothed value while the meter is instantaneous. I imagine I need an RMS value from the Micro Motion.
First Any advice on how to extract or generate the value?
Second, how would one compute the uncertainty of the computed value and the flow meter RMS value?
I am trying to determine whether ratio control with the computed values or the RMS values will reduce downstream variability induced by the feed control & pump system. (Best would be to replace the two pumps with a duplex or multiplex proportioning pump so that the flows are in sync and the mass ratio controlled by stroke length, but I do not have that option near term.)
I would like to take advantage of the constant volume characteristic of the pump to compare the flow generated by the pump to the flow measured by the cmm, as a plausibility check of the health of the cmm and pump. In a sense an on-line prover.
This seems straight forward: stroke speed*volume*cmm density where volume is the calibrated volume @ a stroke setting. However the computed value is in effect a smoothed value while the meter is instantaneous. I imagine I need an RMS value from the Micro Motion.
First Any advice on how to extract or generate the value?
Second, how would one compute the uncertainty of the computed value and the flow meter RMS value?
I am trying to determine whether ratio control with the computed values or the RMS values will reduce downstream variability induced by the feed control & pump system. (Best would be to replace the two pumps with a duplex or multiplex proportioning pump so that the flows are in sync and the mass ratio controlled by stroke length, but I do not have that option near term.)