dtse86
Mechanical
- Sep 9, 2009
- 24
We are currently in the process of starting up an open system with large Armstrong Inline Pumps (~100hp). The pumps are currently controlled by the BAS through VFDs. The balancer has now come in and claims that he is hearing cavitation as he ramps up the pumps and that we are not meeting the NPSHR (27'H2O). Through our calculations we have calculated a NPSHA of ~40'H2O. With the pumps off, he is claiming that the pressure on the suction side of the pump is only ~18'H2O. Something here doesn't seem right and I had personally ramped up the pumps to full capacity and only heard a little noise from the volute. The majority of the noise at that time was coming from the motor. Is there a rule of thumb to determine at what decibel level we can assume cavitation?