pump head calculation for series and parallel pipe networking

Status
Not open for further replies.

PankajMTech

Chemical
Oct 30, 2011
1
Dear all

How to calculate pump head for cooling tower pump 100 m3/hr flows from 6”pipe at 8 m height (existing).
Cooling water uses in three different places

1. Surface condenser 20 m3/hr around 300 m distance, static head 20m pipe size 4” and water back to same height again.(0.6 kgf/cm2 drop in condenser)

2. Chilling system (VAM machine) 60 m3/hr around 250 m distance, static head 2m pipe size 4” and water back to same height again. (0.8 kgf/cm2 drop in system)

3. Crystallizer 20 m3/hr around 500 m distance, static head 8m pipe size 4” and water back to same height again. (1 kgf/cm2 drop in crystallizer)

If we use less head pump (35-40 mtr head) it will able to pump require flow in each pipe?

How to maintain flow distribution?

What will the procedure to calculate pressure drop in this pipe networking?

This is close circuit is there siphon concept also?
 
Replies continue below

Recommended for you

Use Crane TP 410. Its $60.


If we use less head pump (35-40 mtr head) it will able to pump require flow in each pipe?
You need to calculate head loss in each of your runs to see if this is possible, the crane manual has detailed examples.

How to maintain flow distribution?
Use flow control valves. You need to have extra pressure in your system because throttled valves reduce pressure.
 