Pump Head

Status
Not open for further replies.

supaman79

Mechanical
Jul 26, 2004
56
Guys,

When calculating the pump head on a closed chilled water closed loop....should I add all my pressure drops for my chilled water coils, or just my largest P.D.. I would assume just my largest, having that they're not in series. Can anyone help? Thanx
 
Replies continue below

Recommended for you

only the index circuit is required so your assumption is correct

note: sometimes the highest pressure loss circuit is not the index. If you have one 100m long with a pipe loss of say 100kPA and coil PD of 10kPA, you could have a separate parallel circuit of only 50m long and 50kPA loss with a high coil loss of say 70kPA giving it a loss of 120kPA which is the index loss. (unusual but possible)

cheers