We have a general purpose 3HP, 3ph, 60Hz 460V induction motor driving a centrifugal pump for a chiller system pumping water/glycol mix. The motor is started across the line from a MCC bucket roughly 20 feet away. The motor has been recently tripping out on overload. The motor has a FLA of approximately 4.5A (I do not have the nameplate information with me at this moment). We metered the motor current and voltage at the MCC and have observed that the current magnitude in phases L2 and L3 reaches to about 8.5A before the overloads trip. L1 is always steady at ~4.3A. This measurement was repeated multiple times with the similar results. Our electricians decided to swap to a new motor with same nameplate information and same manufacturer. With new motor in place we observed same results - always high current on L2 and L3 before overload trip. We decided to take the measurements closer to the motor at the motor terminals. Upon observing the same results at motor terminals we also noticed that the small part of shaft that was visible between the motor and pump coupling would actually stop rotating. We were able to repeat the results and confirm that the rotor actually stalls when L2 and L3 read about 8A on the meter and right before the overload trips. No questionable noise is heard during this condition. It was also noticed that sometimes the motor would start rotating and slow down to a stall, while at other times it would not even start rotating before tripping the overloads. The chiller and pump supplier confirmed the pump curves and assured us that the 3HP motor is adequately sized. This brings up questions that I hope people on this site with similar experience or ideas can help explain.
1. Why is the current in locked rotor condition only about 2x the FLA
2. Why is the current only high on 2 of the 3 phases and always the same two phases for an overload condition? Shouldn’t we be seeing large current on all three phases?
3. Can inappropriate use of motor be the cause of stall? I am suspicious of general purpose motor being used in this application since the motor is mounted in vertical position with DE bolted on top of the pump. I do not know if the correct type of bearings are used for this application?
I am very interested to see if others have had similar issues. Thanks in advance!
"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic ù and this we know it is, for certain ù then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". û Nikola Tesla
1. Why is the current in locked rotor condition only about 2x the FLA
2. Why is the current only high on 2 of the 3 phases and always the same two phases for an overload condition? Shouldn’t we be seeing large current on all three phases?
3. Can inappropriate use of motor be the cause of stall? I am suspicious of general purpose motor being used in this application since the motor is mounted in vertical position with DE bolted on top of the pump. I do not know if the correct type of bearings are used for this application?
I am very interested to see if others have had similar issues. Thanks in advance!