Hello all,
I work for The town of Paxton, Light Dept. We have a problem at a water pumping station that I,m having trouble with. We have one circuit in town, 13,800 volts grounded wye. The pump station has a 45kVA 3 phase pad transformer with a delta 240/120 secondary (Xo bushing is provided for 120 volt load in pump building, ie lights, scada, teleometry, comm. radios.)
Problem: Water dept. is consistently burning up variable speed drives, boards inside of scada control box, radios, isolation xfers. It seems like, when the town has a dip in power due to a fault/recloser operation, that these problems arise.
Could this occasional loss of power and/or delta secondary configuration with a wild leg be causing a surge when re-energized?
I will provide any needed info to help diagnose the problem.
Thankyou
Chris
I work for The town of Paxton, Light Dept. We have a problem at a water pumping station that I,m having trouble with. We have one circuit in town, 13,800 volts grounded wye. The pump station has a 45kVA 3 phase pad transformer with a delta 240/120 secondary (Xo bushing is provided for 120 volt load in pump building, ie lights, scada, teleometry, comm. radios.)